Low Selector Switch (LSEL)

Low Selector Switch (LSEL)

Low Selector Switch (LSEL)

(OP)
Attached is the Process Control Loop. I would like to know how the Low Selector Switch work.

Thanks.

RE: Low Selector Switch (LSEL)

It picks the lowest of the two signals from PIC and LIC and passes it to FIC to operate on.  To make it work as intended, the action on PIC must be reversed.  If level is low, more feed is needed, and CV opens.  If pressure is low, CV needs to close to raise pressure.  Opposite action is needed on the two signals.

Good luck,
Latexman

RE: Low Selector Switch (LSEL)

The sketch with the valve failure position added would also clarify the control details.  Also, my initial view would desire more controller scheme definition.

I don't like the scheme as shown if both level and pressure controllers were simply PID (proportional, integral, derivative).  With a simple PID scheme, the outputs from both pressure and level controllers would be fighting for the flow setpoint rate.  A control algorithm with both high and low setpoint brackets (no output change when within limits) on each pressure and level would seem like an improvement.  I have not played with the recent DCS algorithms but setpoint bracket configuration would exist.

RE: Low Selector Switch (LSEL)

The simple PID schemes could also likely work.  The setpoint brackets could make the flow control flatter.  The horizontal vessel could narrow the level setpoint scheme such as between 40% and 60% of the level measurement.  Also determine whether the feed is liquid, two-phase or vapor that is condensed.  Such issues could impact the pressure scheme in an interesting manner.

Consider overrides via a safety control system. Normally the operator can select the controller on automatic mode that ignores the level and pressure controllers + the low output selector.  Trip the pump on low level.  Trip the inlet valve on high level.  ...

RE: Low Selector Switch (LSEL)

The turn-down ratio for this drum may be required to considered.
The bigger turn-down ratio of the drum, the large control range  control valve may be required, and the smaller turn-down ratio to the drum, the smaller control range control valve may be required.

 
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources