some what concealed space
any one ever use this section??
if so what circumstances??
how was it installed??
how many lines/ heads??
nfpa 13 2002 edition
8.14.1.5 Localized Protection of Exposed Combustible Construction or Exposed Combustibles. In concealed spaces having exposed combustible construction, or containing exposed combustibles, in localized areas, the combustibles shall be protected as follows:
(1)     If the exposed combustibles are in the vertical partitions or walls around all or a portion of the enclosure, a single row of sprinklers spaced not over 12 ft (3.7 m) apart nor more than 6 ft (1.8 m) from the inside of the partition shall be permitted to protect the surface. The first and last sprinklers in such a row shall not be over 5 ft (1.5 m) from the ends of the partitions.
(2)     If the exposed combustibles are in the horizontal plane, the area of the combustibles shall be permitted to be protected with sprinklers on a light hazard spacing. Additional sprinklers shall be installed no more than 6 ft (1.8 m) outside the outline of the area and not more than 12 ft (3.7 m) on center along the outline. When the outline returns to a wall or other obstruction, the last sprinkler shall not be more than 6 ft (1.8 m) from the wall or obstruction.