Sewer Lift Station: steep slope inlet pipe or inlet free fall?
(OP)
For a sewer lift station with duplex centifugal pumps in the wetwell I am unsure of the best option for the gravity inlet pipe. I only have about 20 LF of pipe between a screen plant and the wetwell. I want to avoid turbulance in the wetwell created by the gravity inlet. I can either have the inlet pipe at a mild slope to decrease inlet velocity but have a 4-ft freefall or have a steep slope (25%+) with the IE at the pump off elevation. In one scenario I have a free-fall which may entrain air and in the other scenario I will have a high inlet velocity(12 fps+) which could create turbulance.
My thought is to avoid free fall and go with the steep slope and install a baffle on the outlet to reduce turbulance/swirling. Any other ideas or thoughts? (The wetwell is going to be 10-ft dia., inlet directed to center of the two pumps).
My thought is to avoid free fall and go with the steep slope and install a baffle on the outlet to reduce turbulance/swirling. Any other ideas or thoughts? (The wetwell is going to be 10-ft dia., inlet directed to center of the two pumps).





RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
Jgailla - This is a new wetwell so we can design the inlet and wetwell as needed. The need to provide emergency storage is the driving factor for the depth of the wetwell in this case and the proximity and elevation of the upstream screen plant dictates my elevation drop.
The "drop bowls" look like a good option to reduce air entrainment but is there any advantage to design a drop inlet rather than a lower steep pipe inlet (other than some cost saving on pipe excavation)?
It seems the steep pipe may be better to reduce air entrainment and the inlet velocity might be similar in both cases because of the drop.
Does anybody have experience with any problems because of steep inlet pipes into the wetwell. Would pre-swirling be an issue in a 10' dia wetwell with the pipe aligned with the center of pumps?
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
Run the pipe at typical slope and step down at a 45deg close to the wet well.
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
The 12 f/s velocity is way too high. The 4 ft drop is probably not a problem but if you are concerned about it, install a drop manhole before the lift station.
Get yourself a copy of Pumping Station Design by Robert L. Sanks before you do any design.
This subject is covered in depth in this comprehensive book.
ht
This book should be on the shelf of every sanitary engineer.
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
RE: Sewer Lift Station: steep slope inlet pipe or inlet free fall?
"Sharing knowledge is the way to immortality"
His Holiness the Dalai Lama.
http://waterhammer.hopout.com.au/