Overhead Transmission Line

Overhead Transmission Line

Overhead Transmission Line

(OP)
I want to size (ampacity)of the conductor for an overhead transmission line at 115kV . For 37MW and then for 74MW. Is there like a "short" way of doing this just to get a "ballpark" type/size.

RE: Overhead Transmission Line

Reference:
1. Fink D.G., Beaty H.W. "Standard Handbook for Electrical Engineers," 13th Edition, McGraw-Hill, Inc., page 461
37MW
37000kW/(sqrt3 x 115kV x 0.9PF x 0.95EFF) = 217.26 A
Aluninum Cable Code Word "Poppy"
AWG Size 1/0
235A at 40 Degree C conductor rise over 40 degree C ambient
74MW
74000kW/(sqrt3 x 115kV x 0.9PF x 0.95EFF) = 434.50 A
Aluninum Cable Code Word "Peony"
AWG size 300MCM
455A at 40 Degree C conductor rise over 40 degree C ambient

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources