Do we normally provide 81L/H protection settings for utility feeders at 13.8kV?
Thanks
Thanks
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
81L/H Settings for Utility Feeders
|
RE: 81L/H Settings for Utility Feeders
81L-Perhaps is you have local generation and could island-load shedding
RE: 81L/H Settings for Utility Feeders
RE: 81L/H Settings for Utility Feeders
If there was no electricity there would be no internet. Good point, don´t you? :D
RE: 81L/H Settings for Utility Feeders
Also, I've never before seen reference to 81H or 81L, the standard usage is 81O and 81U.
RE: 81L/H Settings for Utility Feeders
Do you have unusual loads that could be damaged by over/under frequency? That might be an argument in favor of such protection.
Do you already have the protection hardware installed and its just a question of enabling the functions? Then I'd say maybe.
You might want to talk to your utility and see what their settings are and get their input. Your setpoints could be set outside of theirs as backup protection. And it will give them a heads up to anticipate possible problems if you do drop load during some system anomaly.