Is my 5 ton scroll compressor bad? - electrical readings inside
5 ton 230 v single phase R22 residential A/C compressor
Copeland Scroll type compressor
RUUD system - circa 3/99
with compressor leads unhooked measuring with a Fluke 87 digital VOM.
First is a measurement lead to lead.
R to S - many mega ohms - around 7 M ohms but it climbs the longer you hold it.
R to C  - .6 ohms
C to S - many mega ohms - around 7 M ohms but it climbs the longer you hold it.
Second is a measurement between each lead and the compressor base.
R to base - around 7 M ohms
C to base - around 7 M ohms
S to base - around 1.9 M ohms
Is my compressor bad?
If it is, is it possible it has contaminated my lineset and a-coil with acid?
RE: Is my 5 ton scroll compressor bad? - electrical readings inside
Typical C to S are around ~ 5 ohms and C to R ~ 2 ohms and S to R about 7 so what your reading is almost an open winding at 7 M remember you have to have all the power wiring disconected before you take your readings. I dought that you have a burn out