CMU wall over existing slab

CMU wall over existing slab

(OP)
The Arch wants to place 10'tall 4" & 6" cmu walls (ungrouted, interior) over an existing 4" slab. I am apprehensive even though the slab pics seem to indicate a decent condition of the slab. Am I being too conservative?

Kaiser

RE: CMU wall over existing slab

Probably.  CMU partitions are often built on existing slabs without adverse affect.  The load spreads through the slab, so you will have a strip at least 10 or 12" wide resisting the wall load.  You need to make sure the wall is braced at the top, and can span vertically between the slab and top bracing.

RE: CMU wall over existing slab

Hokie's response assumes that the slab is still fully supported by the earth below it.  You'll want to do a test pit at the location of the wall to ensure that the soil hasn't settled away from the slab.  You could always cut the slab at that section and pour a new thickened slab under the wall.  Yes, it's partition, but it will likely end up taking some of the load, and 10' of wall ain't light, either.

RE: CMU wall over existing slab

(OP)
Thanks fellas. I think I am going to have them rip out the existing slab, replace with a 5" slab and have them put the cmu on the new slab. Usually I use thickened slabs but there are too many walls if I go with 4" slab and thickened slab, that will just make things difficult in the field.

Kaiser

RE: CMU wall over existing slab

I just had a similar situation, Typically I don't like CMU walls on slabs less than 6". We showed on our plans that new hunched slabs at CMU wall locations, but made a note that the contractor to verify the thickness of the existing. slab. basically if we find the slab is about 6" or greater than we will let them dowel into the existing slab rather than but in a hunched slab or a strip footing.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close