EMF Calculation Question

EMF Calculation Question

EMF Calculation Question

(OP)
I need to calculate transmission line induced EMF for a project I am working on.  There are two transmission lines in the same corridor where power flows in opposite directions.
The question is: Do I have to represent one current as negative since they are flowing in opposite directions?

Thanks in advance!

RE: EMF Calculation Question

That's correct, each phase current on your southbound line will be 180-degrees from its corresponding phase on the northbound line.
 

RE: EMF Calculation Question

If you are doing this in PLS-CADD, be sure that you check where each each electrical phase is, which may be different than the structural phase designations.  For example, two identical structures on the right of way may be numbered 123 123, but really have electrical phases ABC CBA.

RE: EMF Calculation Question

(OP)
Thanks for the help, I have a similar follow up question.

I need to calculate the neutral return current, for example A, B, and C phase at 0, 240, and 120 Degrees respectively, have 255.4, 257.5, and 250.3 amps, respectively.  When you add the phasors you will have 6.4 amps of neutral current at 283.9 degrees.

My question, if you're still awake: Do I need to subtract 180 degrees from this neutral current, since it will flow the opposite direction of the phase current?

RE: EMF Calculation Question

Yes.

RE: EMF Calculation Question

If you draw out your circuit, with the 3 phase currents summing to 6.4 A @ 284 degrees, that represents the current into the node.  The outgoing current is what flows through the neutral back to the source.  For your EMF calcs, since the arrows for the phase currents are in opposite directions to the neutral current, you need to shift the neutral current by 180 degrees if you are basing the calc on them all flowing in the same direction.

You can see this better if you just deal with a single phase case.

BTW, my transmission lines don't have neutrals.  This would be  distribution line.

RE: EMF Calculation Question

(OP)
Right, I thought I needed a 180 degree shift.  I am not aware of any transmission lines that are wye-connected with a neutral.  I was referring to a distribution line.

RE: EMF Calculation Question

If you will invert the star of the phasors you'll get
180, 60 and -60 degrees with respect to the old A.
Then the neutral will be 6.413 A at +76.47 degrees.
If they are the same currents in opposite sense !  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources