Single Inlet FDC

Single Inlet FDC

Single Inlet FDC

(OP)
13 2010 6.8.1.3 states that I can use a single butt fdc where the riser is 3" or smaller.  I was sure there was a code reference somewhere stating that the fire dept. supply line had to be at least the size of the riser, but I can't find it in the 2010 edition.  I'm thinking I am good to go with a 3 x 2 1/2 mech tee off the riser and a 2 1/2 check valve.  This is one of those times the electronic version with the keyword search would come in handy!

Thanks in advance.

RE: Single Inlet FDC

Check out section 8.17.2.3 in the 2010 edition.

RE: Single Inlet FDC

(OP)
perfect, thanks bksprinkler

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources