Pulse Output

Pulse Output

Pulse Output

(OP)
I am trying to create a spec for a power meter installation. We want to be able to remotely monitor the power consumption through an existing on site controls system. The meter that has been purchased is an ITRON Sentinel power meter. The only communication output capable of working with the existing system would be the pulse output from the meter. My question is how to interface the meter's pulse output and the control system? Does anyone have any good info/resources on pulse output.

From what I was able to find it is basically a square wave where each pulse represents a value of Wh multiplied by a certain factor, ie. 1 pulse is 1Wh. I am not a controls expert but would this mean that if 1 pulse occurs in an hour the consumption is 1Wh, 1000 pulses per hour is 1kwh? I would assume that you need some time range to determine the actual consumption but nothing I have read states this. As well I can't seem to find anywhere that specs a mode of interface. Would it be just a 18awg pair cable? twisted/shielded/unshielded? cat5? 2 conduct? Thanks in advance for the help.

RE: Pulse Output

The pulse is a consumption unit, meaning 1 pulse = ? kWh

RE: Pulse Output

You do not need any time range to determine the actual consumption of ENERGY.  The pulses will give you the consumed energy.  However, if you require the RATE of energy consumption, then you'll need the time base.

 

RE: Pulse Output

(OP)
Thanks for the help guys, much appreciated.

RE: Pulse Output

You may find that the KYZ output is coded and does not at all output pulses that you can count. That happened to me in several cases. You then need to sense the blinking LED in the front. You can do that with any photo transistor and a suitable pull-up resistor. Ten kohms and 5 V works well.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Pulse Output

Depending on the distance between the devices,
Would it be just a 18awg pair cable? - Yes

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources