Condenser Intake and Discharge Duct Separation
Condenser Intake and Discharge Duct Separation
(OP)
We have a project that use an indoor condenser. The intake and discharge are ducted to a Building Louver. They share the same louver. The intake and discharge duct are 1 foot apart, edge to edge. Do you need to separate the ducts? If so, how many feet?





RE: Condenser Intake and Discharge Duct Separation
RE: Condenser Intake and Discharge Duct Separation
If there is a prevailing breeze the discharge should be downwind.
If you can't count on a breeze then the discharge should have a sufficiently high velocity to achieve dilution quickly, and should be directed away from the intake.
RE: Condenser Intake and Discharge Duct Separation
RE: Condenser Intake and Discharge Duct Separation
The louvres will deflect it down, but it will turn and rise again taking it away from the intake.
B.E.
RE: Condenser Intake and Discharge Duct Separation
If you ever can, you should make additional louver to supply make-up air for room, and duct exhaust only.
RE: Condenser Intake and Discharge Duct Separation
@mechengncpe - "I think no less than about 3000fpm on the discharge would prevent short circuiting."
Do you suggest making the discharge duct a little bit smaller to achieve 3000fpm? Would that increase the noise?
RE: Condenser Intake and Discharge Duct Separation
intake duct is 30x24. velocity is 1200 fpm.
RE: Condenser Intake and Discharge Duct Separation
An application engineer at Titus once told me when I was going through a similar issue that you can visualize it with a match. "It's easy to blow a match out... but you ever try to 'suck' one out?" <insert inappropriate but well deserved comments now>
Just get your discharge velocity up enough to satisfy the equation and you should be fine.
www.ellisconsultingengineers.com
RE: Condenser Intake and Discharge Duct Separation
RE: Condenser Intake and Discharge Duct Separation
Found this:
The combination intake/discharge
louver design offers an advantage
over separate louvers because
it requires only one wall opening
which decreases installation costs.
However, the blades cannot be
of uniform configuration (i.e. the
same blade design and angle). The
discharge louver blades should be
angled to direct the airflow straight
out horizontally from the unit and
the intake blades should be angled
down at approximately 45°.
RE: Condenser Intake and Discharge Duct Separation
High velocities undoubtedly create effective dilution which is useful in many exhaust application, and even necessary in some.
In this particular case, however, one other aspect could be relevant - high velocity creates ejection effect.
Whatever jet pattern exhaust flow develops, there will be lateral streams and the one on side of intake lover could significantly reduce effective area of intake opening.
I am not sure whether HVAC Applications manual mentions it, but combined louvers were mostly related to limited flow applications