Protection CT - Choosing a CT based on your Max Fault Current

Protection CT - Choosing a CT based on your Max Fault Current

Protection CT - Choosing a CT based on your Max Fault Current

(OP)
Good Afternoon,

I need help in determining whether the CT we have meets the fault requirements.
The CT is a 1000:5 5P20 30VA Protection CT - I have a saturation curve with a knee point at 140V. Rct (Secondary Winding res.) = 0.245 @75C
The max fault I need to design for is 32 kA.
I understand that the correct CT will need to operate at 32kA without saturating i.e. before the knee point.

How can I determine this ?
I appreciate all the help.
Thanks Again
Coren

RE: Protection CT - Choosing a CT based on your Max Fault Current

To figure this out, you also need to know the burden of the relay and round-trip leads (Rb).

Vsec = 32 x 5A x (Rct + Rb) < 140V

Works out to being ok if Rb < 0.63 ohms.  

RE: Protection CT - Choosing a CT based on your Max Fault Current

(OP)
Thank you very much for the info Scott - just a quick question for you:

If the knee point is measured @140V with I=0.124A giving the measured CT burden at 17.36VA.
As the CT is rated at a 30VA burden - is it safe to estimate that the CT can handle a current 34.56 times the Primary (20 * 30/17.36 = 34.56) =~34kA prior to saturation ?

Unfortunately at this time I dont yet know Rb - would the above derive a good estimate/indication ?

Thanks Again
Coren

RE: Protection CT - Choosing a CT based on your Max Fault Current

It all boils down to what you call "saturation".

The rating of 5P20 - 30 VA means that the error won't exceed 5% at 20 time over-current when loaded at 30 VA.

20 x 5A = 100A
5% of 100A is 5A, which means excitation current can't exceed 5A up to a secondary voltage of (30/(5^2)) * 100A = 120 V

The CT was measured with an Iexc=0.124A at 140V, so it meets the class by a good margin.

With all that said, you still need to know your Rb to confirm what over-current the CT can handle without saturation. There really isn't any other way to do it correctly. You can certainly approximate it for a good estimate. You need the lead wire size, the round-trip lead length, and the relay input impedance. If it's a modern electronic relay, then it can really be ignored, since the leads will dominate the burden calculation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources