lightecho (Mechanical)
11 Apr 11 17:29
I have a building with 22 year old QR sprinklers that I will send out for UL testing as per 25, 5.3.1.1.1.3.
I thought there was a recommendation of how many per 100 or percentage in 25. I sure don't see it now.
Thx
Dave
NJ1 (Mechanical)
11 Apr 11 21:45
NFPA 25-2002
5.3.1.1.1.2 Sprinklers using fast response elements that have being in service for over 20 years shall be tested. They shall be retested at 10 years intervals.
5.3.1.2
A representative sample of sprinklers for testing per 5.3.1.1.1 shall consist of a minimum of not less than 4 sprinklers or 1 percent of the number of sprinklers per sprinkler sample, whichever is greater.