Terminal block for Hazardous area
Terminal block for Hazardous area
(OP)
Anyone please advise
there is a terminal bock inside lighting junction box EEx'e' installing in Hazardous area.
I need to know that require pin lug for cable connection in this terminal blocks or not?
And If without pin lug what will happen when energise.
Note this terminal block is screw type,
thanks
there is a terminal bock inside lighting junction box EEx'e' installing in Hazardous area.
I need to know that require pin lug for cable connection in this terminal blocks or not?
And If without pin lug what will happen when energise.
Note this terminal block is screw type,
thanks






RE: Terminal block for Hazardous area
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Terminal block for Hazardous area
RE: Terminal block for Hazardous area
Your box is EEx"e" type which means "increased safety" design.Therefore,the terminal block has got extra creepage distances to avoid sparks.Therefore,use normal lugs if it is a stranded conductor and wire normally.There cannot be special wiring methods.