Cogeneration and Fault Mitigation
Cogeneration and Fault Mitigation
(OP)
Looking to limit the amount of fault current back to the grid from our cogeneration plant.
Woudl like to use inverters as the fault mitigation. Anyone know if there are inverters out there in the 13.2kv range and a rating of 2.5MW - 3MW?
Thanks.
b
Woudl like to use inverters as the fault mitigation. Anyone know if there are inverters out there in the 13.2kv range and a rating of 2.5MW - 3MW?
Thanks.
b






RE: Cogeneration and Fault Mitigation
Why do you think you need to do this?
David Castor
www.cvoes.com
RE: Cogeneration and Fault Mitigation
RE: Cogeneration and Fault Mitigation
David Castor
www.cvoes.com
RE: Cogeneration and Fault Mitigation
RE: Cogeneration and Fault Mitigation
How about air core reactors?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Cogeneration and Fault Mitigation
If there is not large motors or not concern with large voltage dip in the system, a series current limiting reactor may be a good option to consider to limit the SC.
Depend on the characteristics and operation mode of the system, a MV VFD could be a cost effective option if additional saving can be justified operating motors at variable speed and HP under the rated max. nameplate for reasonable time.