SLG bracing and interrupting ratings on 69 kV outdoor sub

SLG bracing and interrupting ratings on 69 kV outdoor sub

SLG bracing and interrupting ratings on 69 kV outdoor sub

(OP)
We have an existing 230 - 69 kV substation that is rated for 40 kA on the 69 side. We are looking at building a second sub on the south side of the refinery that will operate with a 69 tie between the two stations, keeping them in parallel. Our studies are showing a SLG fault level of 39 kA. How does this relate to the 3 ph rating of the existing station?

Thanks,

Jim

RE: SLG bracing and interrupting ratings on 69 kV outdoor sub

You don't say what is rated 40 kA.  Equipment like switches don't care whether the current is 1Ø or 3Ø.  Bus bracing is for 3Ø or Ø-Ø faults; 1Ø faults generally don't create much force on buses.  Grounding systems don't care about 3Ø faults, only Ø-grd faults.
 

RE: SLG bracing and interrupting ratings on 69 kV outdoor sub

(OP)
The bus bracing is 40kA and the interrupting rating on the breakers is also 40 kA.  My concern is on the breakers.  We are hearing the older versions of the ANSI standards allowed for a higher interrupting rating on breakers for SLG faults over 3PH, but we are pulling the newer standard to see if this still applies.  I thought I might pose the question here to get some other opinions.

RE: SLG bracing and interrupting ratings on 69 kV outdoor sub

There are several possibilities out there for doing breaker rating studies, typically in the same software packages used for doing the fault studies.

RE: SLG bracing and interrupting ratings on 69 kV outdoor sub

The available short circuit of 39 kV is very close to the equipment rating. Check if a series reactor could help to reduce the SC current or consider a 63 kA breakers for your application.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources