Heat Gain (sensible kw) from dryers calculation
2

Heat Gain (sensible kw) from dryers calculation

Heat Gain (sensible kw) from dryers calculation

(OP)
Hello experts,
I've been trying to calculate the sensible heat gain from a commercial dryer for the past two days but no positive results. Can someone here guide me on how it can be done. Thanks

RE: Heat Gain (sensible kw) from dryers calculation

What is the input?

Gas or electric?

Heat gain will be a percentage of input.  

RE: Heat Gain (sensible kw) from dryers calculation

The simplest method would be to call the manufacturer and ask them.   

RE: Heat Gain (sensible kw) from dryers calculation

550 MBH input, 3600cfm

Qs=cfm*1.08*(dt)
Qs=3600*1.08*(70)=272MBH bringing air from 70degF to 140degF, now if the discharge temp is higher, you will have less gain to the room, as your dT will be larger.  

550MBH-272MBH=278MBH gain.  See what the outlet temp is and you will have it.   

RE: Heat Gain (sensible kw) from dryers calculation

Sensible heat equation is not good enough.

It's a drier remember.  You are vaporizing maybe 40 pounds of water in the process.  You need to work out the latent process as well.

Then energy balance approach will work of course, you just need to account for all of the energy.

RE: Heat Gain (sensible kw) from dryers calculation

oh thats right, sorry, Qt=4.5*cfm*dH

RE: Heat Gain (sensible kw) from dryers calculation

Does a 23 ton sensible load seem high?
 

knowledge is power

RE: Heat Gain (sensible kw) from dryers calculation

(OP)
Awesomw thanks guys.. this should do

RE: Heat Gain (sensible kw) from dryers calculation

Depending on the installation, the heat gain to the occupied space may be negligible.  The body of the dryer will be in the back of house space where all of the combustion/make-up air is (can be) introduced.  Cycle time of the dryer will impact things, but for worst case you can assume they are all running constantly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources