S7-300 to ControlLogix over Ethernet

S7-300 to ControlLogix over Ethernet

S7-300 to ControlLogix over Ethernet

(OP)
I am looking to get data from a Siemens S7-300 to a ControlLogix PLC over Ethernet.  The Siemens rack has a CP-343 module and the AB rack has an ENBT.  Every search I've done tells me I need some sort of protocol converter, but I haven't seen any pertinent info that's recent.  Does anyone have any experience with this?

RE: S7-300 to ControlLogix over Ethernet

You need a protocol converter. The CP343 is profibus and the A-B ENBT is Ethernet. The Data Station Plus from Red Lion is I think the easiest and most intuitive converter to program on the market, but not the cheapest. Free software lets you pick protocols and ports from drop-down menus, click, boom, done.
http://www.redlion.net/Products/HumanMachineInterface/DataStationPlus/DataStationPlus.html
 

"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: S7-300 to ControlLogix over Ethernet

(OP)
Thanks for the feedback.  I'm looking at the specs on the Siemens card (CP-343-1 "Lean") and it says TCP/IP, and it has a RJ45 port.  Would I still need the converter? (the ENBT is Ethernet/IP protocol).

RE: S7-300 to ControlLogix over Ethernet

Yes, you still need a protocol converter.  The Siemens module talks in ProfiNet, and the AB module talks in DeviceNet.  Both protocols use Ethernet as media, and TCP as transport protocol.  But they have DIFFERENT grammar at application layer.  They won't understand each other.

BTW, do not confuse Allen Bradley EtherNet/IP with TCP/IP.  EtherNet/IP stands for 'Ethernet Industrial Protocol'.

RE: S7-300 to ControlLogix over Ethernet

Your best bet is to use an ethernet EWEB module in your contrologix processor.  The siemens processor can talk straight generic ethernet.  That is the only way to talk directly to each other without a protocal converter.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources