Hi there,
We are planning to install a 5kV TECK 90 Cable buried in a cable trench. One of the client requirements is that any cables buried in a cable trench in a vehicular area needs to be installed in a rigid steel conduit.
Now, my question is whether a 5kV TECK 90 cable can be installed in a rigid steel conduit underground. Is this a common practise among industrial clients?
I was told that the 5kV TECK 90 cable can be damaged during cable pulling if installed in a conduit.
Comments anyone?
Thanks in advance.
We are planning to install a 5kV TECK 90 Cable buried in a cable trench. One of the client requirements is that any cables buried in a cable trench in a vehicular area needs to be installed in a rigid steel conduit.
Now, my question is whether a 5kV TECK 90 cable can be installed in a rigid steel conduit underground. Is this a common practise among industrial clients?
I was told that the 5kV TECK 90 cable can be damaged during cable pulling if installed in a conduit.
Comments anyone?
Thanks in advance.






RE: 5kV Teck 90 Cable in Rigid Steel Conduit
I would not say it is common, but it is sometimes done. Just mind the bending radius.
David Castor
www.cvoes.com
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
Teck cable is generally installed in conduit to provide extra mechanical protection.
Consider bell ends on the conduit instead of bushings. Beware of dirt and stones entering the conduit with the Teck cable.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
It is a 5kV TECK 90 3C-500MCM Non-Shielded cable. This cable has a total diameter of 2.78 inches (including the outer jacket). My concern is the cable bending of that cable in a rigid steel conduit underground (i.e. buried trench).
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
If you want more guidance on design on the conduit system, I'd contact your local Okonite office. They like to find ways for people to use more C-L-X so are generally helpful. (No affiliation.)
David Castor
www.cvoes.com
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
I do not have my book with me. Maybe someone can verify this.
RE: 5kV Teck 90 Cable in Rigid Steel Conduit
Since "Teck Cable" is a CSA spec, I'm assuming this work is in Canada.
David Castor
www.cvoes.com