effect of exceeding maximum piping length in split type aircon

effect of exceeding maximum piping length in split type aircon

effect of exceeding maximum piping length in split type aircon

(OP)
what is the effect when you exceed maximum piping length on split type air-conditioning units? is there a range in exceeding the range in the manufacturer's specification regarding piping length.  

RE: effect of exceeding maximum piping length in split type aircon

Pressure drop increases and capacity is reduced.

RE: effect of exceeding maximum piping length in split type aircon

Refrigerant piping is different from hydronic systems, if you exceed lenght too much, it can happen that expansion valves on evaporators (indoor units) will not work.

Exact allowance is deeply related to manufacturers, I had lot of such circumstances and found out that different manufacturers state different tolerances, someone's recommendations are on safe side, some are not. You would need to talk with manufacturers technical support if you want to come to the exact limits.

RE: effect of exceeding maximum piping length in split type aircon

^ Agreed. Ask your local sales rep. for a Long Line Design Guideline.

Also, be concerned with proper oil return to your compressor(s).

RE: effect of exceeding maximum piping length in split type aircon

no warranty!!!!
 

RE: effect of exceeding maximum piping length in split type aircon

Trap the lines as per manufacturer recommendations.  There are volumes of installation guidlines for this.  Good luck.

RE: effect of exceeding maximum piping length in split type aircon

Pressure drop increases, flashing increases, capacity decreases.
Velocity decreases limiting lubricant return ruining compressor.

RE: effect of exceeding maximum piping length in split type aircon

All are right on the money.  Carrier offers the best data I have seen on the drop in capacities vs. length of refrigerant run.  Worth taking a peak at - as I remember it being quite significant when you start exceeding 200 feet equivalent length.   

RE: effect of exceeding maximum piping length in split type aircon

(OP)
you mean if the piping limit for example is 60 ft for a 2.5 hp wall mounted split type, the drop in capacity will be significant if you install it exceeding 200 ft?  

RE: effect of exceeding maximum piping length in split type aircon

If you read the fine print, units are typically rated with 5m (say 15ft) of pipework.  I would guess 60ft on a 2.5hp wall mounted split would have a effect on capacity, and 200ft would have a significant impact on capacity.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources