measurement of transformer zero sequence impedance
measurement of transformer zero sequence impedance
(OP)
how to measure (test) the zero sequence impedance of two winding, three phase Dyn11 33/11 kV 15 MVA transformer?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
measurement of transformer zero sequence impedance
|
RE: measurement of transformer zero sequence impedance
RE: measurement of transformer zero sequence impedance
- 3 phase at delta side to be shorted together.
- 3 phase at y side to be shorted together.
- apply the voltage between one of the phases at y side and nutral.
- Z0 will be equall to V/I