Electric damper actuators

Electric damper actuators

Electric damper actuators

(OP)
I have a project where I've been asked to control a electric damper actuator, specifically

http://www.valvesolutions.com/pdf/gca%202p.pdf

using a 0-10VDC signal for positioning.  I've been looking for some sort of document that discusses the 0-10V control but haven't been successful yet.

Questions really are...0-10V equates to a position?  This is only the control, separate from the actuator voltage, or is it the same?  The cut sheet really doesnt lend itself to explaining how to use the device.

If this is the wrong forum, let me know...wasnt sure this or the PLC forum.

  

RE: Electric damper actuators

It's a 2 position valve - opened fully or closed fully.  It's not meant to be partially open.

RE: Electric damper actuators

(OP)
OK, so 0V is closed, 10V is open, I don't need to actually ramp over the voltage.  I was thinking this was a damper where you can control the air flow based on the positioning of the valve.

RE: Electric damper actuators

That damper can not use a 0-10V signal. It is a open-closed unit that uses either 24VAC or 120VAC. You can find other units which would be suitable for a position control application.

 

RE: Electric damper actuators

(OP)
OK..makes more sense, I need to go back to the customer..who spec'ed this part and ask...you sure about this?

RE: Electric damper actuators

Is this a new version of the left handed wrench? Either by mistake or malicious intent, you have been given a spec sheet for an actuator that is not compatible with 0-10VDC control.
Look at the device sending the 0-10VDC signal. Reprogram it for on-off control and then use an interposing relay to switch the power to the actuator. You will still have on-off control of the actuator. If you need to modulate the damper you must change the actuator.
http://valvesolutionsinc.thomasnet.com/item/non-spring-return-siemens-actuators/-return-direct-coupled-electronic-damper-actuato-3/geb161-1u?
This damper still requires power as well as a 0-10VDC, 2-10 VDC or 4-20 mA DC control signal. (a 500 Ohm resistor across the control terminals will convert 4-20 mA DC to 2-10 VDC).
BUT BEWARE! Fire codes or environmental concerns may require a spring return damper that will automatically close when power is lost. You may have to keep the spring return damper and forget modulating the position.
 

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Electric damper actuators

They also make spring return actuators that can be modulated when powered, but spring return to a "fail safe" position.

RE: Electric damper actuators

Spring returns in electric actuators are limited because the electric mechanism has to first overcome the force of the spring return before it can apply any force to the driven load.  For that reason they don't tend to get very large in my experience at least.

rmw

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources