Question about reinforcing existing beams
I have a question. My structural software is giving me answers that don't seem to make sense. I'm trying to add a W section to the bottom of some existing W16x40's to reinforce them for a mill that's in the room above.
Now I first tried adding a WT, and a little WT6x13 worked. But the contractor wants to use a W instead, so I'm trying some. One with an equal flange width and thickness is a W6x20, so I tried that but it failed, by a lot. I've been trying bigger and bigger sections, but they're not working. What is so fundamentally different about having the W section's extra flange's worth of steel in there that would make it fail like that when the WT worked?
RE: Question about reinforcing existing beams
Is this an analysis program?
You would think it would be easy, but there must be some compactness criteria or some other thing that I'm missing which is causing the beam to be analyzed by a different equation or something, because it's so counterintuitive that a beam with a higher moment of inertia would be failing in bending when a beam with a lower I is passing.
All of these questions will help you get a better answer.
For problems like you're doing now, I typically use RAM Elements (used to be RAM Advanse) as an analysis tool only and design the reinforcing and welds by hand based on the analysis results provided by Elements.
There are no shear studs in the concrete, so it's just the beam acting on its own.
Another question I guess is how do I even go about designing this by hand? The code is very clear in telling you how to design a single beam, but when you're stacking two different beams, I don't see anything regarding that in section F. Is it in a different chapter? If not, which member's tw do you use in checking it for compactness and all that?
If I can find it I will post it on the Web, but it is really not a difficult calc.
AISC 360-05 doesn't really address this for LTB, but if you have an small unbraced length I wouldn't worry about it. If your unbraced length is something longer, you can use the green book to determine an allowable bending stress.
How did you intend to check RAM Elements output if you don't know how to design this by hand?
The way I would normally design it by hand is I would find an allowable stress based on section F. Then I would check the actual stress and compare it to the unity check in section G. Right? Just like a regular beam.
I must be overlooking something though, because I still don't understand why adding the W section causes RAM to think the beam fails when the WT does not. Adding the W gives it a higher section modulus than the WT.
Michael.
Timing has a lot to do with the outcome of a rain dance.
With the WT section added, the top and bottom flanges are comparable. With the W6X20 section added, the top and bottom flanges are not. As a result, with the WT section, the NA is likely to be pulled lower than the W6X20 section, not decreasing the stress in the top flange as much.
How did you model the connection of the W6X20 to the existing beam? Not being truly an integrated member with only welding at the periphery of the flanges could be a problem, even though there is not much contribution to the composite I from these members. I wonder if the program is reading a buckling of the top flange of the W6X20 member?
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
Are you jacking any of the stress out of the existing beam before you reinforce it? That is one of the biggest factors in the analysis of the section.
Paddington and Msquared, thanks, that seems plausible.
1) Determine the stress in the beam with the DL, call this fb1. This will be the moment that is currently in the existing beam divided by the section modulus of the unreinforced steel
2) Determine the section properties of the new, composite section
3) Determine the stress at the top of the composite section (top flange of existing beam), call this fb2. This will be the superimposed moment divided by the section modulus (to the topo of the section) of the reinforced, composite beam.
4) Determine the stress at the bottom of the composite section (bottom of the reinforcement), call this fbt. This will be the superimposed moment divided by the section modulus (to the bottom of the section) of the reinforced composite section. Verify this is less than the allowable. This rarely, if ever, controls the design.
5) Add fb1 and fb2, this is the net compressive bending stress in the existing steel. Verify this is less than allowable (you'll probably have to use the green book to get an allowable). This is what usually controls the design.
6)Determine the required cutoff point for the reinforcement. This will be the location on the bending moment diagram where the total moment (existing and superimposed) does not exceed the capacity of the bare, unreinforced section.
7) Design the skip welds for VQ/I (stagger the welds on each side of the web of the WT reinforcement
8) Extend the WT past the cutoff point by a length that will develop the WT and design the weld to develop the WT in that extension zone.
If you are simply popping in two WF beams from two nodes, the program may be only loading one of the beams and not the other. Software usually doesn't have the ability to deal with non-common shapes like that. Can you explain how you are modeling this in RAM?
RAM Elements allows you to input a lot of custom sections - one of them is two WF stacked as a single, composite member.
Jay-
I just popped one in as a simply supported beam and did a design check. The design report references F4.2, which is appropriate. Now that I look at F4.2, it actually uses the same radius of gyration of the compression portion of the member as does the 9th edition (green book). The overall equation isn't identical, but it gives similar results.
My guess is that the WT was just barely working and the WF was just barely not working. I'm sure it has something to do with the section properties of the built-up section just working out a little differently.
The WF will drag the ENA lower on the composite section, which will put more of the web in compression. This will result in a lower rt in eq. F4-5, which results in a lower Fcr.
This is only true for LTB. If you have closely spaced bracing this shouldn't be governing your design. What are your bracing conditions?
STAAD has a similar facility for stacked beams.
The output in STAAD shows you exactly the equations and values used in the code check.
Like M^2 is suggesting, if the NA is actually such that the top flange of the W6x20 is in compression (doubtful by looking at it) and your parameters for the W6x20 are such that the unbraced length is the full 20' beam length that could be your problem.
Does RAM allow you to assign a parameter to "tell" it the W6x20 top flange is braced?
Does Ram see this as truly a single member?
I'd be curious to compare it to STAAD...I have never used STAADS double member facility.
Check SteelTools.org
It would be check if nothing else ( I hate using spreadsheets I didn't write or check)
I am going to guess that there is an error with the input into RAM Elements. Your sketch says the W16x40 + WT6x13 has a D/C = 0.26 (demand/capacity). While the W16x40 + W6x20 has a D/C = 1.5. That would indicate that the built up section with the WT has almost 6 times the capacity! For another reality check, what is the D/C for the W16x40 alone?
RAM Elements has nice output. It will give you the section properties of the sections. It will also provide the beam's capacity for each limit state checked with a reference to the specification section.
Thanks PA for all your help. The beam isn't laterally braced at all, bottom or top. According to the contractor, the deck apparently just sits on top of the beam, which is a shame, because the composite section probably would have passed.
I've attached the report from RAM on the 16x40 alone if you'd like to look at it. I'll post the reinforced-with-WT and the W reports in the next 2 posts.
As it turns out, they can't use the reinforcing I designed anyway, because of utilities that they don't want to move, which are 4" below the beam. So I tried another section, A C10x20 welded to the bottom flange, and by some reason that's just as perplexing as these other sections, it comes out passing with a ratio of 0.26.
I really need to figure this out. These problems come up all the time.
That doesn't quite make sense to me and I would do a hand calc of J for each case to see if it matches what RAM is spitting out.
For the 16x40 alone, Ix=518, Iy=28.9, and Jz=0.794?
What's wrong here?
But the W16x40 alone I come up with 0.743, which isn't so far wrong from RAM's number of 0.794, and is likely right considering I ignored the fillets.
What the heck is going on here? Is my program hosed?
If anyone has the updated RAM Elements, could you check if your numbers are right for J? Because I'm still running RAM Advanse. Maybe it's time to update.
They're usually pretty good about fixing problems and pointing you in the right direction if there is a problem in their software. 1-800-778-4277, prompt 7, then prompt 2.
JWB
I can help you determine exactly why your reinforcements work or don't in RAM Advanse. Please contact me directly to discuss.
Due to forum rules I cannot post my e-mail here, but I am sure you'll find a way to contact me.
Thank you!
BA