Are conduit or pipe threads used in Class 1, Div 1 Enviroments?
2

Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

(OP)
I am not clear on which type of dies to use threading 1/2" conduit for a Class 1, Div 1 installation. My understanding is that conduit threads are "straight threads" for mechanical construction, and that pipe threads are tapered for sealing. The NEC 346-8 refers to ANSI B.1.20.1. Is there something I missed in the NEC or ANSI B.1.20.1 that states which treads should be used?

RE: Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

All conduit threads are required to be tapered threads.  Conduit couplings use straight threads, but the conduit itself uses the same threads as plumbing pipe.  344.28 (348-8 in the '99 code)in the NEC requires all field cut conduit threads to have a 3/4" to the foot taper.

Don

RE: Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

2
Other supporting verbiage:

99NEC500-3. General.
 (d) Threaded Conduit. All threaded conduit referred to herein shall be threaded with an NPT standard conduit cutting die that provides 3⁄4-in. taper per foot. Such conduit shall be made wrenchtight to prevent sparking when fault current flows through the conduit system, and ensure the explosionproof or dust-ignitionproof integrity of the conduit system where applicable.
  

RE: Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

A field note...
If you are preparing a spec for conduit, please do add that an anti-seize compound be applied to all threads prior to final assembly.
cheers.
a.

RE: Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

Good point, Abeltio.  The 2002 code requires an approved conductive corrosion protective coating for all field cut threads in area where the conduit requires corrosion protection.  See 300.6(A).
Don

RE: Are conduit or pipe threads used in Class 1, Div 1 Enviroments?

You said that "344.28 (348-8 in the '99 code)in the NEC requires all field cut conduit threads to have a 3/4" to the foot taper." Does this also apply to factory threaded conduit?

RE: Are conduit or pipe threads used in Class 1, Div 1 Enviroments?


http://www.alliedtube.com/grc.pdf Column 1 calls out the ¾-inch-per-foot taper and ANSI B.1.20.1.  It’s very likely that listed galvanized-steel and aluminum conduit and IMC have the same characteristics.  The details would probably be described in the corresponding UL standard.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources