Flange Hydrotest pressure (EN1092-1)
I referred to EN 1092-1-2007 standard for hydrostatic test pressures & test duration of PN designated flanges. However I could not find any such reference in that standard.
If I recall correctly old versions of applicable DIN standards for steel flanges used to mention minimum test presure equal to 1.5 x maximum working pressure of flange at 20°C as per P/T rating.
Can anyone help me with this?
Thanks in advance.
RE: Flange Hydrotest pressure (EN1092-1)
You are right, 1092-1 doesn't mention anything about hydrotesting.
In ASME B16.5 regular flanges doesn't need hydrotesting, but flanged fittings do and I think it works the same way in the EN world.
Thanks Raaden for your reply. I need to have a basis / reference from EN standard to justify the hydro test pressures & test duration of a PN rated flanged fitting or valve. Very often such references are required to convince the local inspection authorities.
Would you be able to help me further with this?
Thanks.
Well a flanged valve is tested according to EN 12266-1 with the following pressure:
"The test pressure (see A.1.6) shall be a minimum of 1,5 times the allowable pressure at room temperature."
Annex E.3.2.1 gives you insight in the calculation method for some flange types.
"-at assembly and testing 200 MPa (Ptest = 1,43 × PN)."
So it seems you should use a higher PN-rate when your pressure testing becomes higher that 1,34xPN.
Kelly
Kelly, can you elaborate on your statement about 1,34xPN?
The 1,43PN is taken directly from the PED and that pressure will create a stress in the material that can be up to 95% of the yield strength of the material, which also happens to be what most EN standards specify as their max allowed stress at test condition. So I would say that you only need to worry about the test pressure when it gets higher than 1,43PN.
Raaden,
Referring to the statement:-
I was wondering if there is any limit specified in standards on the maximum allowable hydrotest pressure.
Please comment.
The only limiting factor for the test pressure is that the membrane stress in the part shall not go above 95% of the yield stress (90% in ASME) during testing.
Sorry, the 1,34 is a typo. Should be 1,43.