Reduction in roof live loads
A co-worker and I were having a discussion on reductions in roof live loads and the appropriate tributary areas to use. If I have 8' o.c. trusses on a 60' wide building, the tributary area for the truss is 480sf. For live load, using 480sf, I calculate a reduction factor R1 = .72. That is very simple. However, when I look at the reaction that the truss places on an isolated column, I tend to think that I must use a live load reduction of .96 since my tributary area is now 240sf. Is that correct?
Assuming that is correct, how then do I look at the reactions from the truss on a girder that is 30' long? Is the tributary area that I use to determine my R1 for the concentrated loads at 8' o.c. on the girder equal to 1/2 the building width multiplied by:
1. Girder length of 30'?
2. Actual tributary width of roof carried by the girder?
3. Truss spacing of 8'?
4. Other??
It makes a huge difference how you look at it, and I'd appreciate some perspectives on this.
Thanks.
4. Other??
Thanks.
RE: Reduction in roof live loads
So the answer to your question is 2.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
BA