transformer conductor calculations
transformer conductor calculations
(OP)
If I have a 3 phase transformer rated at 30kVA, 600V primary, 120/208V secondary:
Ip=[30x1000]/[600x1.73]=28.9A (then multiply by 1.25 for code) and the cable size would be #8AWG
Is=[30x1000]/[208x1.73]=83.3A (then multiply by 1.25 for code) and the cable size would be #2AWG
And for a 1 phase transformer rated at 30kVA, 600V primary, 120/240V secondary:
Ip=[30x1000]/[600]=50A (then multiply by 1.25 for code) and the cable size would be #6AWG
Is=[30x1000]/[240]=125A (then multiply by 1.25 for code) and the cable size would be #1/0AWG
I'm going by Table 2 in the CEC for cable size and 90 deg. rated. Is this correct? I'm out of my element on this one. Just wondering if there is other factors I missed. The breaker on the primary would be set to trip to protect the cable (125% primary rated current).
Thanks,
thenoob
Ip=[30x1000]/[600x1.73]=28.9A (then multiply by 1.25 for code) and the cable size would be #8AWG
Is=[30x1000]/[208x1.73]=83.3A (then multiply by 1.25 for code) and the cable size would be #2AWG
And for a 1 phase transformer rated at 30kVA, 600V primary, 120/240V secondary:
Ip=[30x1000]/[600]=50A (then multiply by 1.25 for code) and the cable size would be #6AWG
Is=[30x1000]/[240]=125A (then multiply by 1.25 for code) and the cable size would be #1/0AWG
I'm going by Table 2 in the CEC for cable size and 90 deg. rated. Is this correct? I'm out of my element on this one. Just wondering if there is other factors I missed. The breaker on the primary would be set to trip to protect the cable (125% primary rated current).
Thanks,
thenoob






RE: transformer conductor calculations
For a primary breaker, it is also necessary to account for the transformer inrush current. If you size the breaker strictly per 125% of the transformer FLA, a molded case breaker can trip on inrush. I'm guessing you'll want at least a 40 A primary breaker and the conductor must be sized for a 40 A breaker. If it was me, I'd put in a 50A breaker. But I'm an NEC guy. For 480 V primary breakers on 30 kVA transformers, I use a 60 A breaker. NEC allows primary protection sized up to 250% if secondary protection is provided.
David Castor