SCCR Explanation

SCCR Explanation

SCCR Explanation

(OP)
I'm having difficulty understanding the theory behind an SCCR rating being applied only to a specific combination of devices.  A current limiting fuse for example interrupts the current in 1/4 cycle.  So the maximum current seen by any device in series with that fuse should be whatever the value is at 1/4 cycle.  

Why then can we only use UL approved combinations?  It seems to me that the current limiting fuse will interrupt the current at 1/4 cycle, regardless of what other devices are in series with it.  The SCCR rating should be based upon the fastest protective device.  

I understand that I am wrong, but I don't understand why I am wrong.  Does anyone have any insight?

RE: SCCR Explanation

The reasons are both technical and reglulatory (codes), especially in the USA.

1. The current limiting fuses are not current limiting at all currents, only at high currents.

2. UL (or equivalent nationally recognized testing lab)'s listing is a code requirement, whether it is standard SCCR
or series rating. UL will only provide a label if the devices (or combination there of) pass the test.

3. There is no approved calculation method to determine series rating (contrary to what any fuse mfr. might say).

In reality, if you check any published series rating tables by a reputed mfr, you will find that most MCCB are series rated with various types or class of fuses (RK, J, L etc), regardless of the manufacturer of the fuses. While the breakers have to be listed with a specific model number & mfr.  

So what you are hoping to have is already in place, except that you need to verify that it is indeed a listed combination.
 

Rafiq Bulsara
http://www.srengineersct.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources