Ignoring transmission impedance in network models

Ignoring transmission impedance in network models

Ignoring transmission impedance in network models

(OP)
Why do some utilities simulation tools ignore the transmission impedance in network models for its analysis? I understand that it will increase the voltage drop and it would not allow proper sizing of conductors. But, it is necessary for sizing of breakers at substations and other devices, also for faults at the station buses.   

Regards,

Reynaldo Salcedo

RE: Ignoring transmission impedance in network models

I don't understand. What kind of network model would ignore the transmission impedance?  How could a model of the transmission network ignore the transmission network elements?
 

RE: Ignoring transmission impedance in network models

Yeah, what jghrist said.  No "solution" tool that would ignore something as critical as transmission impedance is worth using.

RE: Ignoring transmission impedance in network models

(OP)
That is exactly the same thing that I was thinking. I believe that only loadflow could (might) be done under those conditions, and that is only assuming that the voltages are considered from head of feeders and completely ignoring the substation.

Regards,

Reynaldo Salcedo

RE: Ignoring transmission impedance in network models

When dealing with radial circuits you can always lump everything upstream into the source impedance.  That isn't ignoring the transmission impedance, it is just lumping it with everything else upstream of the substation.

RE: Ignoring transmission impedance in network models

(OP)
Thanks a lot for your answers, I thought for a second that the way I was thinking about modeling a distribution system was wrong.  

Regards,

Reynaldo Salcedo

RE: Ignoring transmission impedance in network models

It is common in MV and HV neglect the resistance and consider the impedance as pure reactance. Probably this may be the issue.

Occasionally a source could be consider as an infinite bus (zero impedance) just for simplification. However modeling network with negligible impedance does not sound right without additional explanation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources