Temperature Derating factor

Temperature Derating factor

Temperature Derating factor

(OP)
Hi,

I'm working in a power station where the ambient temperature is close to 55 deg C.What derating factor could be used for the loading of the generators? I know that the best way to obtain the derating factor is from the supplier but the generators are very old stuffs and I'm looking for a reasonable factor.I presume a ten degree rise in working temperature is considerable.The generators are of 5000 kVA size.

Guardiano

RE: Temperature Derating factor

That's very hot. Does the generator nameplate give an ambient temperature for the rating?  Normally it would be 40 deg C.  

Is the generator air-cooled?   

David Castor
www.cvoes.com

RE: Temperature Derating factor


Assuming that the old windings are of class B insulation, 120 degrees C would be the maximum operating temperature according to most standards. Therefore, at 40 degrees C ambient the permissible temperature rise would be 80 K. If the ambient temperature is 55 degrees C, then the maximum operating temperature still is 120 degrees C but the permissible temperature rise would be 65 K only. Make sure that site elevation is less than 1000 metres above sea level, otherwise the temperatures mentioned above have to be reduced.

Wolf
www.hydropower-consult.com

RE: Temperature Derating factor

Does the generator have winding RTDs?   

David Castor
www.cvoes.com

RE: Temperature Derating factor

Yes, wolf39 is right. The deciding point is not the ambient temperature but the total temperature (ambient + rise). The generator's insulation temperature rise and temperature class is the deciding factor. This information should be provided on the nameplate for larger generators.

I agree with wolf39 that you will probably find that you have a Class B insulation which allows a stator temperature of 120C. This corresponds to 40C ambient + 80C rise.

If you have RTD's (dpc's question) then you can determine if your generator is running too hot.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources