How much would you need available to test the above transformer?
The site if fed from 630kVA 415 transfomer which is good for 800Amps. They have allowed for a 500A supply to this.
Any assistance is apprecaited.
Thanks,
The site if fed from 630kVA 415 transfomer which is good for 800Amps. They have allowed for a 500A supply to this.
Any assistance is apprecaited.
Thanks,






RE: Testing of a 1MVA 400V to 11KV Step Up Transformer
If you are interested in Acceptance tests, most field test equipment can operate from single phase 115/230V 10 A supply.
You may require three phase power for fans, depending on design.
RE: Testing of a 1MVA 400V to 11KV Step Up Transformer
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Testing of a 1MVA 400V to 11KV Step Up Transformer
However, they want to use a 1MVA 400V to 11KV transformer from a 415V, 500A supply. The transformer will be then used for testing transformers. this is not enough power is it?