Power plant synchronization to transmission system

Power plant synchronization to transmission system

Power plant synchronization to transmission system

(OP)
I understand that its standard to opearate a transmission system within 5% of a rated voltage.  Can power plant be synched to transmission system at any voltage within 5% of rated as well, or should it be synched at rated voltage?

RE: Power plant synchronization to transmission system

The generator voltage is adjusted to match the line voltage. A range of +/- 5% is manageable.  In most cases the generator will be operating at a slightly higher voltage than the incoming line so that it can supply reactive power to the grid.  

 

David Castor
www.cvoes.com

RE: Power plant synchronization to transmission system

in some European countries Grid Codes it is specified to synchronize to the grid at 0 MVar unless otherwise instructed
 

May you grow up to be righteous, may you grow up to be true...

RE: Power plant synchronization to transmission system

(OP)
Thanks for your swift reply, dpc.  Can you recommend a text or reference manual that speaks to this situation?   

RE: Power plant synchronization to transmission system

IEEE Standards C50.12 and C50.13 provide specifications
for the construction of cylindrical-rotor and salient-pole
synchronous generators, respectively. They specify,
"Generators shall be designed to be fit for service without
inspection or repair after synchronizing that is within the
limits listed..." [1] [2]. The limits for both types of generators
are:
• Angle ±10 degrees.
• Voltage 0 to +5 percent.
• Slip ±0.067 Hz.
IEEE Standard 67, which also discusses synchronizing
requirements, specifically says that the standard does not
apply to the prime mover [3]. The author is unaware of any
standards that apply to the design of the prime mover, so the
generator limits are typically the ones used to design a
synchronizing system. However, in practice, wider limits are
often applied because the prime mover control is not fine
enough to reliably achieve a 0.067 Hz slip.
................H

extracted from
Fundamentals and Advancements in Generator Synchronizing Systems


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources