asce 7-05 drifting and sliding snow
I have a long (40' per side)shallow pitched (4:12) gable roof that drops down (8 ft) to a 30' long flat roof. I am developing a truss loading diagram for the flat roof area. The question is do you combine balanced snow + drifting snow + sliding snow or do you treat balanced + drifting as one case and balanced + sliding as another and take the worse case?
RE: asce 7-05 drifting and sliding snow
I'm surprised no one has answered this question.
I would not consider balanced + drifting + sliding as one total combination.  The last sentence of ASCE 7-07 section 7.9 states "Sliding loads shall be superimposed on the balanced snow load."  It does not mention superimposing the sliding snow on the snow drift.
In this case, I would look at windward drift + balance snow, leeward drift + balance snow and sliding snow + balance snow.  I would also not consider a mineral surfaced roof slippery (if you have one).
This is how I interpret this section you need to do the same.
At the wall projection between the flat and gable roofs I would have a triangular load distribution.  For the altitude of the triangle, I  would have the height of that wall and the base of the triangle would be about 1/3rd of the flat roof; for snow density, I would use wet snow value.--My two cents.
You should review ASCE - Guide to Snow Loads by Dr. Michael O'Rourke.  He is the chairman of ASCE7 snow load chapter.  Good reference.