My question is: Are these systems only needed if the building is sprinklered?
I have a private hydrant that is being furnished on-site, but the building is not sprinklered. To use the Detector Check System makes no sense to me in this circumstance. The detail has a 4" diameter in/out line which would make sense going to a private fire system (sprinklers), but not to a hydrant which requires a 6" diameter feed.
I have a private hydrant that is being furnished on-site, but the building is not sprinklered. To use the Detector Check System makes no sense to me in this circumstance. The detail has a 4" diameter in/out line which would make sense going to a private fire system (sprinklers), but not to a hydrant which requires a 6" diameter feed.
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask





RE: Detector Check System Requirement
In our system we have properties that have fire hydrants but no sprinkler system. We require double detector check valves on these fire systems. The reason we require this is because there have been many instances where they have a leak on their underground piping and no one would know, except for the detector on the double check assembly. We have also had people use the fire hydrants to wash off their parking lots or for other unauthorized use. Again, we would not know except for the detector. We constantly have discussions with property owner's that feel our requirements for a double detector check on just a fire hydrant system is unwarranted, but our experience has shown otherwise.
RE: Detector Check System Requirement
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
RE: Detector Check System Requirement