(OP)
Is there a phase difference in the signals on two wires connected to one leg of a delta configuration 115 Vac 60 Hz power source?  What should be measured across the two wires?  What should be measured from each wire to ground?

RE: Single Phase Power

Please, would you rephrase the posting in therms of two signals on two wires. This would normally imply a multiplexing or some other processing of two signals.

RE: Single Phase Power

Depends on what you are measuring - & against what reference.  
Define your delta triangle as ABC, with the phase you are concerned about being AB.  If you use BC as the reference, then AB will show an angle of 120 degrees lead, BA will show 60 degrees lag.  With CA as the reference, then AB will show an angle of 120 degrees lag, BA will show 60 degrees lead.

As far as readings to ground are concerned, that depends on whether the delta is grounded or not.  If it isn't grounded, then the (balanced) system capacitance will establish a neutral point roughly at the centre of the triangle.  Again using BC as the reference, A-g will show a lead angle of around 90 degrees, while B-g will show a lag angle of around 30 degrees.
With say the C corner of the delta grounded, A-g will show 60 degrees leading, with B-g showing 0 degrees against BC reference.
If the midpoint of say BC is grounded, then A-g reads 90 degrees lead and B-g reads 0 degrees against BC reference.

The key is that you need to establish a proper reference to measure against

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources