Cutting a 10kV bus bar
4

Cutting a 10kV bus bar

Cutting a 10kV bus bar

(OP)
We have to cut a small section (about 3 feet) of our non-seggregated 10 kV bus bar (all three phases) since the ends are not aligning with the bar holes at the generator end (other end of the bus bar is connected to the transformer low voltage bushing stubs). Instead of cutting the bar at the end and machining new holes, we want to cut it in the middle and reconnect it (bolt or weld). The alignment issue came because of wrong calculation on dimension (this is a new installation).
Does anybody see any problem with cutting the middle section of the bus bar and reconnecting it?
Much appreciated.

 

RE: Cutting a 10kV bus bar

Copper is a nightmare to weld, especially in the field, which from a practical point of view leaves you with making a bolted joint. A bolted joint is never going to be as good as a solid bar, which is what you would have if you drilled the bar end. Is it a particularly awkward task to drill the bar?
 
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Cutting a 10kV bus bar

Copper or aluminum?
IPS?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Cutting a 10kV bus bar

Good point Bill, aluminium would be a lot easier to deal with. Oops!
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: Cutting a 10kV bus bar

one thing i had done with the same problem last year that joint the two bus bar segment with flexiable bar but the section was of ngr,in case of outgoing which carry havey current, any patch give you local heating

RE: Cutting a 10kV bus bar

At 10 kV, regardless of how simple it looks, have a professional switchgear manufacturer how deals with medium voltage gear assembly do the job. The stated approach sounds too causal to me.

Rafiq Bulsara
http://www.srengineersct.com

RE: Cutting a 10kV bus bar

Sounds like a potential source of local PD activity.  

RE: Cutting a 10kV bus bar

(OP)
Thanks all for the answer. It is copper bus by the way.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources