Static Exciter Field Cables
Static Exciter Field Cables
(OP)
I was recently told that the field cables for Static Excitation Systems need to be rated for 10 time (10x) the max exciter voltage... is that true?... is it in an IEEE Spec somewhere?
For example, I'm spec'ing a cable a for a static exciter field run that will have 240 V (nominal) and 360 V (max). Do I need a 4 or 5 kV cable?
I've looked in my IEEE standards, surfed the websites of cable and exciter manufacturers, and searched on Eng-Tip but to no avail.
Any help will be appreciated.
Thanks,
CaptElectron
For example, I'm spec'ing a cable a for a static exciter field run that will have 240 V (nominal) and 360 V (max). Do I need a 4 or 5 kV cable?
I've looked in my IEEE standards, surfed the websites of cable and exciter manufacturers, and searched on Eng-Tip but to no avail.
Any help will be appreciated.
Thanks,
CaptElectron






RE: Static Exciter Field Cables
I'm kind of curious where the 10X transients would be expected to come from...?
-John
RE: Static Exciter Field Cables
The crow-bar circuit should stop the worst of the over voltages that might occur.
RE: Static Exciter Field Cables
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Static Exciter Field Cables
RE: Static Exciter Field Cables
This could account for the test level rating of your exciter cable, which is a part of the rotor circuit.
Muthu