PFC Capacitor with Backup Generator as Voltage Regulator

PFC Capacitor with Backup Generator as Voltage Regulator

PFC Capacitor with Backup Generator as Voltage Regulator

(OP)
Does it make sense to use a PFC capacitor bank to maintain my household voltage level when using a generator of about 8.5kVA on my 200 amp electrical service?  I have a 3/4 HP well pump and a 3 ton central air unit along with the rest of the usual appliances running on this service.  Lights dim momentarily when pump or air comes on.  Also are there any risks associated with doing this.  I would placard my meter base so utility workers would be aware.

RE: PFC Capacitor with Backup Generator as Voltage Regulator

Just accept the voltage sag.

RE: PFC Capacitor with Backup Generator as Voltage Regulator

Capacitor or no, an 8.5kw generator is not going to be as stiff as typical utility power.  

RE: PFC Capacitor with Backup Generator as Voltage Regulator

PFC caps would not prevent the voltage sag anyway. Either live with it as davidbeach said, or install a Soft Starer or VFD on the well pump. That may be problematic for 1 phase loads however and the largest being an A/C compressor may make it impossible anyway.

By the way, the "quick and dirty rule of thumb" on generator sizing when starting motors across-the-line is kVA = 3x connected HP. You have almost 4HP connected to that generator, you should have bought a 12kVA. You are not going to avoid a sag when they start and if they start at exactly the same time, it may not happen at all.

"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: PFC Capacitor with Backup Generator as Voltage Regulator

Quote:

I would placard my meter base so utility workers would be aware.
This is unacceptable and dangerous. It could have serious legal repercussions for you, even if there are no incidents. In the worst case scenario you may be responsible for the death of a utility worker.
Please have a qualified electrician install an aproved transfer switch.
Adding capacitors to a generator may lead to over-voltages and instability and possible damage to the generator and to connected equipment.
As far as the motors, if they are starting, re-read David Beach's post concerning the voltage dip.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: PFC Capacitor with Backup Generator as Voltage Regulator

Suggest to ask for the generator reactive capability curve to see the generator capability. Try to avoid capacitor in the generator system. You would experience some difficulties.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources