Fire walls / design in plant
Dear sirs,
We are looking at our design codes and finding a seperation distance requires us to deluge a tank ~15 meters of flammable plant. Due to layout issues the management of the run off water causes issues and secondary containment design. so..
one concept we are evaluating is the consideration for a fire wall (clearly to discuss/ confirm with local codes/insurers etc.) but i'd like some feedback on the use of them in plants.
are the concrete or can steel be acceptable.. ive seen solid floor from steel act as a fire barrier for say air cooled condensers.. but dont know if it applies to fire walls.
RE: Fire walls / design in plant
The Firewall is mostly an inside barrier.
The main methods of tank Fire protection is drainage of liquids
(no pool fire) and exterior insulation.
One application where outdoor fire walls are used to prevent the spreading of a fire is in the protection of Main Transformers at power plants.
Usually, you will find a three sided design used to protect the turbine buiding from a fire generated by the transformer.
The transformer is also usually placed above a pit where transformer oils can drain, should there be an accident
http:
http://www
POwer and Water Engg