I have a 90 hp 400v 130A electric motor in my installation. the line voltage is average 170v on phase to neutral. in other words low line voltage is being experienced. what mehod do you guys think i could adopt to solve this problem. will a transformer do? if yes what type?






RE: what is the solutiom
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
Chinese prisoner wins Nobel Peace Prize
RE: what is the solutiom
Why is the line voltage low? Is it low only when you run the motor or is it low before you start running the motor?
Is the power supply big enough to supply the motor?
Did you get supplied with the wrong voltage motor and that's what you want to fix?
We need some hints before suppling answers.
RE: what is the solutiom
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: what is the solutiom
Is this a DOL motor or do you have a soft starter or a VFD involved?
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: what is the solutiom
I would double check that the system you're connected to is in fact a 480V grounded wye. If it is, that voltage is cause for concern.