Required thrust lengths overlapping

Required thrust lengths overlapping

Required thrust lengths overlapping

(OP)
I'm looking at the situation described in the attached, where valve A and valve B are both closed.  Pressure beyond each valve is zero.  Treating each end of the pipe as a dead-end, the required thrust restraint lengths overlap.  However, all forces oppose each other.  So if I restrain the entire length of pipe, all situations should be covered -
both Valve A and B closed,
Valve A only closed,
Valve B only Closed.  
This is probably a stupid question, just want to confirm...
Thanks

RE: Required thrust lengths overlapping

You are correct.  If all pipe between valve A and B is restrained, you should be covered if Vavle A and B are closed, or if only one of the valves is closed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources