Transmission of surges through right-angle termination
This would be again considering 0.1 microsecond rise time pulses in a power system. There are two different types of concern:
1 - surges from power system propogating toward the motor.. we'd like to lessen them.
2 - surges generated by partial discharge inside the motor which propogate outward into terminal box, make a right angle turn to get to coupling capacitor filter network for sending partial discharge.
In both cases, there is occasions where the surge may encounter a 90 degree turn in the copper buswork within the terminal box. I'm guessing the buswork is 1/4" thick.
What effect does a 90 degree turn have on pulses that I assume are initially propogating in transverse electromagnetic mode.
What about a 90 degree tap. i.e. surge has the choice to go straight or make a 90 degree turn... will any of it go down the 90 degree tap>?
(2B)+(2B)' ?
RE: Transmission of surges through right-angle termination
Of course yes.
The split depends on the total picture, including what's further downstream in each path.
90° is just 25% of a single turn coil.
If it were shielded conductor or a coil with adjacent turns that provide a well-defined tranmission line, then I'm inclined to believe the pulse has easier time following turns.
In this case, it it is three separate buses about 1' apart from each other and 1' away from ground, undergoing 90 turn with relatiely small radius. It is not obvious to me why that the pulse is going to make the turn since the transmission line path is not well defined by virtue of distance to the ground and other phases. And seems even more of a challenge for wave to make a 90 degree turn at a Tee configuration. I am picturing (right or wrong) that there is something resembling plane wave propogation within the conductor and I wouldn't think a plane wave would change its direction like that.
Do you have any suggested reference on this or further ideas? I'd be interested to hear.
(2B)+(2B)' ?
A pulse is perfectly happy to split into two (or N) parts in accordance with Kirchhoff's circuit laws (adapted to account for impedance and frequency spectrum and so on and so on and so on...). Thinking in terms of "a pulse" may lead one to thinking that a pulse is an entity that is somehow going to stick together and follow only one path or the other. That's obviously not true.
Given a T-junction, it's almost a certainty that some significant fraction of 'the pulse' would be reflected back towards the original source (a perfect Z match being very unlikely). So the pulse split would be 3-way.
(2B)+(2B)' ?
We have TDR instruments that we sometimes use in our work, but we've never even contemplated using them to map out power wiring.
What about a branch connection shaped like a Tee. It has 3 ports: two on the sides of the top of the Tee, and one on the bottom.
Will the behavior be the same in terms of splitting regardless of whether the pulse come in the bottom or come in the side of the top of the Tee?
(2B)+(2B)' ?
I would suspect the answer will be yes based on your previous answers which suggest the behavior is approximated from transmission line theory using surge impedance and not depending on physical geometry features that are much smaller than wavelength (as long as they don't significantly affect surge impedance).
(2B)+(2B)' ?
That makes intuitive sense, but it raises a question:
small compared to what?
Compared to the wavelength? In that case we would judge that the lower-frequency-content pulses (longer wavelength) would see more impedance change for a given bend than a higher-frequency-content pulse....does not sound right.
Compared to the conductor spacing? The example I provided has bend very small compared to spacing to ground and others?
Maybe there is a compound condition implied: "small radius of curvature compared to conductor spacing, but both large compared to wavelength?"
(2B)+(2B)' ?
Exactly, that's why I mentioned "...HF frequency range; so an inch here or there isn't much compared to a wavelength..."
So, what about the bold portion of my quote above? I don't think lower-frequency content pulses will see a larger change in impedance for a given bend radius than higher-frequency-content pulses (do you?). Therefore I think there must be more to the story than comparing bend radius to wavelength.
(2B)+(2B)' ?
Many years ago there was an article in one of the radio hobbiest magazines proposing to use the medium-wave 160m (1.8 - 2.0 MHz) radio band for 'Moon bounce' (EME) because it was "fewer wavelengths to the Moon".
What about the Tee configuration.... does it make any difference whether the pulse comes into the bottom of the Tee or the side/top of the Tee (in terms of the fractions transmitted to each of the outputs and reflected to the input)? (Assuming for simplicity same surge impedance in all branches... terminated with matched impedances... 2"x1/4" copper bus, 0.1 microsecond rise time.)
(2B)+(2B)' ?
This implies the pulse will propagate without much affect from features much smaller than the wavelength.
So the tee won't matter and the pulse will split into any attached conductor.
The important keyword is "much". Perhaps better expressed as "much much".
Quarter wavelength is often maximum effect.
Thanks for helping to straighten me out on that.
(2B)+(2B)' ?
Your analysis should reveal an "impedance bump" directly *at* the right angle turn. I presume due to an increase in the series inductance part of the transmission line model at that exact point.
I have done a very crude 2-D "transmission line matrix method" simulation of a wave launched into a right-angle turn... for two different scenario's:
First: Short Rise time: the rise time is half of the cross section of the conductor.
Second: Long Rise time: the rise time is four times the width of the conductor.
There is a lot more reflection for the short rise time than the long rise time, as expected. I was halfway expecting that the simulation would give some intuition as to why that occurs, but I'm not sure it does.
Attached is the short rise time animation.
(2B)+(2B)' ?
(2B)+(2B)' ?
"Please excuse the crudity of my model...", Dr Emmett Brown ('Back to the Future')
"...the rise time is [X] the cross section of the conductor..." where X = 0.5 or 4
Assuming a sensible rise-time (us scale), that's a fairly wide conductor, isn't it? (Well worth stealing for the copper value; bring a crane and a truck.) Or (for a 2-inch wide bus bar) an extremely fast rise-time (GHz band).
My instinct says that the waveform in the .avi sims is showing way too much 'internal' reflections for the scales to be correctly matched. Almost as if you could shave the corner at 45° to 'bounce' the waveform edge around the corner like a beam of light.
Double-check that the scale of the waveform and the scale of the conductor actually match reality.
To make it easy and general purpose, I tried to model all my boundaries using and impedance mesh. Low impedance in conductor area and high impedance everywhere else including a 1-cell-wide strip around the edges. Then I blocked out the values in the center because they were distracting from the picture. There are some features of the boundaries that are quite obviously not exactly correct like the ridge on the left side of the wave, but I didn't spend a lot of time correcting them... maybe later. Another is that simple 2-D mesh creates anisotropy in the medium (wave propagates sqrt2 faster along the mesh than 45 degrees from the mesh). There is a correction available, but for simplicity I ignored it. There are the reasons I called it crude.
I am well aware of the relationship between rise time and dimension, but the dimensions I selected suited my purposes better (demonstration, not calculation of a magnitude). I don't think that picture of doubling and reflection would have been as clear comparing two rise times which were both many orders of magnitude higher than the width. I learned the speed of light in 3rd grade, and this speed will not be too much lower. But thanks for your assumption that I did not have that 3rd grade knowledge... we all know what they say about assumptions.
(2B)+(2B)' ?
(2B)+(2B)' ?
If the purpose of this exercise is to refine your instincts, then it's best to start in the middle before working out to the extreme cases.
Assuming that the rise time of surge of interest is still around 0.1 microsecond, then your model bent conductor is the size of a building. That's pretty big. It's not that you didn't know that (reading minds is not my specialty), it's that the implications of this extreme scale ratio choice are significant.
The mental construct of an internal "wall", where the waveform bounces around internally, does not exist within correctly (more real-world) scaled conductors. Most conductors are essentially one-dimensional structures, often bent into other dimensions.
If I may re-purpose a famous phrase - Within most conductors as typically applied, "God does not play..." billiards with charge carriers.
To keep the avi file size managable, snapshots are taken every time the wave advances 20 grid points (before it was 5). If you look carefully you can see the leading edge jumping along the path for the first 14 snapshots (1st 5 seconds of avi) and you can see the trailing edge (where it turns constant) passing through between 20 and 25 seconds.
There is no discernible (from the graphic) reflection by this 2-D model even for rise time 1/40 of conductor cross width. How well that related to real life scenarios I'm not sure.
(2B)+(2B)' ?
should've obviously been
(2B)+(2B)' ?
(2B)+(2B)' ?
Sorry.
Do you mind to point out exactly where I crossed the line?
What follows is your discussion where you percieve my simulation to be based on complete ignorance of the scale (*). And to up the comic value of your comments, let's throw in "Well worth stealing for the copper value; bring a crane and a truck."
I hope you can see where that might strike me negatively. At any rate I suspect now it was not intended that way, maybe I just need more sense of humour and lighten up a little.
(*) By the way, I hope you can see that comparing 40xwidth to 4000x width would show nothing at all interesting. The comparison of 1 / 2 width to 4x width showed a lot more that we might possibly learn from the simulation. Relevance of that "learning" to a particular scenario's is an important item to judge and an open question for me.
It may be the case. What is the explanation for the impedance bump that you referred to earlier?
(2B)+(2B)' ?
For right angle bend, there is also the fact that the effective width gets longer as you pass through the turn. But this is seen in the simulation and does not cause any reflection at 40x and beyond.
I wonder if there is some effect similar to self inductance... the wave at position X has different linkage to the wave at position X-deltaX when the line is curved ? That might be mixing quasistatic/field concepts with wave concepts... I'm not sure.
(2B)+(2B)' ?
I would be interested to hear more about what kind of impedance bumps you see... including wiring configuration and rise time of incoming wave.
(2B)+(2B)' ?
It's worth noting that your expertise is held in the highest possible regard by myself and many others on Eng-Tips. In comparison, all that I can offer is the occasional real-world 'boundary condition' that may occasionally guide and constrain the theoretical analysis.
What is "...the explanation for the impedance bump..." of a right angle bend?
Series inductance.
90° is obviously one-quarter of a full turn (excuse the embedded humour, it's unavoidable).
As a gedanken experiment, replace the 90° bend with a very smooth and continuous curve that continues to curl around and around. Make it as many turns as you wish.
It's a coil; an inductor.
Lots of series inductance.
Plenty of 'impedance bump' to restrict (choke) the flow of higher frequencies.
And not a single "wall" anywhere.
Lots of data, geometrical and electrical, plus results from measurements on actual connectors to test different simulations against. The measurements show all aspects you can think of - including TDR.
The phenomenon does not have any practical consequences in power applications where voltage levels are orders of magnitude higher than the voltage induced in the discontinuity. Add to that that rise-times very seldom are shorter than 100 ns in power circuits while sub-ns are met in 'signal' electronics.
Gunnar Englund
www.gke.org
Gunnar - That is pretty much the same conclusion I was reaching. For most purposes the right angle makes no difference in power systems. Compared to computer systems, the dimensions are larger which makes wave effects more likely, but the rise times are lower by a much larger factor which makes wave effects less pronounced.
In contrast, tees/branches should have an effect on pulses even in a power system, although I can understand now that it doesn't make much difference whether you go straight through the Tee or make a turn.
(2B)+(2B)' ?