Fire Sprinkler System (Wet) and Rooftop Manifolds
3

Fire Sprinkler System (Wet) and Rooftop Manifolds

Fire Sprinkler System (Wet) and Rooftop Manifolds

(OP)
In a fully sprinklered medical office bldg. 2-stories with roof access via roof hatch in stairwell, is a roof manifold required? NFPA 14 states the requirement for fire standpipe and combined standpipes, but is a roof manifold ever installed on a wet auto. sprk. system? NY State jurisdiction (not NYC)

RE: Fire Sprinkler System (Wet) and Rooftop Manifolds

The purpose of the roof manifold is to test the standpipe demand and test fire pump at roof if applicable. If you have a fire pump the header should be at street level so that is out of the question. I dont think you need to have a combination system on a 2 storie building.
What is the building spec for?

RE: Fire Sprinkler System (Wet) and Rooftop Manifolds

Find out what building / fire code is in use for that ahj, sometimes thee is a requirement in there that is not in 14

RE: Fire Sprinkler System (Wet) and Rooftop Manifolds

(OP)
You see CDAFD, that's what is bugging me. The town of the project happens to be one of those AHJ's that make teir own requirements. The fire marshal is very stringent in addition of making contact to inquire. NFPA 14 or any other code for that matter is not to specific if it mentions it at all. I was just curious on account of the type of roof access and also gas fired units placed there.
Does anyone know of a specific code (fire, bldg, etc) that specifically states that rooftop manifolds are not required atop of sprinkler risers?

RE: Fire Sprinkler System (Wet) and Rooftop Manifolds

What is the standpipe classification, i.e., Class I, II or III? Since you're in NY state, your answer is found in 2009 IFC Section 905.4, item 5 if it's a Class I standpipe. If it's a Class III standpipe, no roof manifold is required.

RE: Fire Sprinkler System (Wet) and Rooftop Manifolds

(OP)
Thank you. I kind of figured that. I just needed to show it documented to my client. I'm a freelance plbg/fp designer. Thanks again.

RE: Fire Sprinkler System (Wet) and Rooftop Manifolds

(OP)
By the way, it's a class III

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources