MCC powering transformer aux
MCC powering transformer aux
(OP)
I know MCCs are commonly used for providing power to a motor circuit, such as pump or even motor etc. They have the OL/OC protection and starter cicuitry.
Question I have is, can I use one of the bucket from a generic 480V MCC cubicle to provide power for Transformer auxilliaries which do not have motor (such as cabinet heaters etc). I have some pumps and fans which need power from MCC, but I now also need to power my cabinet components (for say 10kA, 120V) so I was thinking of bringing in the 480V-3 phase power from the MCC to a small cabinet and stepping it down to 120V to power the cabinet components.
Anybody sees any problem with it? Hopefully I am not being too vague.
Question I have is, can I use one of the bucket from a generic 480V MCC cubicle to provide power for Transformer auxilliaries which do not have motor (such as cabinet heaters etc). I have some pumps and fans which need power from MCC, but I now also need to power my cabinet components (for say 10kA, 120V) so I was thinking of bringing in the 480V-3 phase power from the MCC to a small cabinet and stepping it down to 120V to power the cabinet components.
Anybody sees any problem with it? Hopefully I am not being too vague.






RE: MCC powering transformer aux
The MCC is the structure, the devices you put into it are up to you. So yes, you can certainly get what is called a "feeder bucket" that is just a circuit breaker in a cubicle that taps power from the MCC bus bars to send to any kind of load you like. Not at all a problem.
If you want to be able to turn it on and off remotely, order a "Contactor Feeder" bucket. it will have a standard thermal-magnetic circuit breaker and a contactor that you can control remotely. it will not have "overload heaters" as you would find on a motor starter.
But if you have an existing motor starter in an MCC, you cannot use that to feed any other load besides a motor. They are not listed (or intended) to be used that way. Likewise you cannot just remove the OL heaters and use it that way, the circuit breaker used in an MCC starter bucket is different and can ONLY be used as part of a motor starter assembly.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: MCC powering transformer aux
At least you still use breaker at feeder outgoing to protect your load and cable.
RE: MCC powering transformer aux
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MCC powering transformer aux
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: MCC powering transformer aux
I have always fed lighting transformers, battery chargers, UPS bypass transformers etc. from 480V MCC's. Just put in a correctly sized molded case circuit breaker, size the cable properly and you're set.
RE: MCC powering transformer aux
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: MCC powering transformer aux
Thanks to Jraef, Danses, Waross, ASimmons23. You guys made this post more than worthwhile.