Dear Members,

Model plumbing codes require indirect piping (air gap) when connecting food handling fixtures to the plumbing system. Typical arrangement for restaurants is: triple sink - grease trap - plumbing system. My question is - where it is preferable to put an air gap - upstream or downstream of grease trap. I saw recommendations to do it immediately after sink (which means upstream), but I doubt if it is going to work, because typical grease trap has flow control fitting upstream. Is it regulated by code?
Any suggestions?

Thank you very much in advance!

RE: Grease interceptor connection question

I don't know where you're located, but the Illinois Plumbing Codes are online.  They include, in Appendix E, illustrations which I believe would answer your questions.  

Google:  Illinois (or other state) plumbing code

Patricia Lougheed

******

Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.

RE: Grease interceptor connection question

(OP)
Dear Patricia,

Thank you very much for the response. I am in New York City, so the plumbing code is a little different and does not have illustrations. I saw the Illinois code but I believe that it does not describe this specific situation. As we know, codes are sometimes unclear.
BTW, if it looks like I violate somehow the rules of the forum (if so, it is really unintentionally), I will stop this thread immediately. Thank you very much again for your help.

RE: Grease interceptor connection question

I believe you are talking about  grease trap. In Florida they required on the waste water lines, not sanitary.  The purpose here is to keep the grease or cooking oils out of the sewer system whether it's a sptic or municipal sewer system.  They are essentially a container that will separate the water from the oil.  On some the oil is fed into another tank and is routinely pumped out.   

I have on one my drains from the kitchen sink just to prevent any grease going into my septic system.

RE: Grease interceptor connection question

They are essentialy just a skimmer, Some of them depending on the design do require a syphon breaker on the downstream side, so that they do not syphon the grease out of the trap.
  The other thing with these items, is to watch the material they are made from. Corrosion and rust through is very common on these, after they are put in service.
B.E.

RE: Grease interceptor connection question

(OP)
Hi Berkshire,

Thank you for valuable notice regarding syphon breaker downstream of the device.

RE: Grease interceptor connection question

You might check the code that is governing the device as the size and type might be regulated.

RE: Grease interceptor connection question

Each state and some municipalities have their standardized plumbing codes.  I just installed a brand-new one in my Pub (my sideline business).  In Minnesota, there is no air gap at the connections, but you need to have a tell-tale floor drain hooked into the system, with vents before and after the grease trap.  Your local public health authority would be the people to contact regarding restaurant and food service installations.  Their codes often augment or take precedence over uniform codes.

RE: Grease interceptor connection question

See what your local codes require. However, keep in mind that these things are notorious for smelling horrible after a while, regardless of how well maintained they are. If at all possible/permittable, pipe continuously with vents before and after the unit.  

RE: Grease interceptor connection question

(OP)
I highly appreciate everyone's valuable responses, thank you very much, the installation configuration is now clear for me. In addition, are there special types of grease traps specifically for chocolate production related waste?
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources