What could cause this?
The panel is 208/120 panel and it appears that the peak voltage is being clipped. Also, the user reported that dimmer switch that was installed would not work on A phase but it worked on B or C. Voltage readings were normal as you can see from the graph.
RE: What could cause this?
I see nothing abnormal. Flat top - caused by SMPS in computers and the like - some mild notching, probably dimmers. No probs at all.
Is the light source dimmable? Some aren't.
Gunnar Englund
www.gke.org
The issue is that this is a country club, they have a lot of lights but not that many computers. Could dimmers really cause this much voltage drop at peak?
Yes, the light source was dimmable. It worked on B or C phases.
Dimmers do not flatten the sine, the notches are probably the result of dimmers (or thyristor controlled drives - very unlikely). Modern appliances flatten sine waves. They also have lots of switch-mode power supplies. Does this country club have their own transformer? Or are there other consumers connected?
Gunnar Englund
www.gke.org