refrigeration evaporator performance

refrigeration evaporator performance

refrigeration evaporator performance

(OP)
My work involves an environmental test chamber (hot, cold & humidity, the issue I have is during cold tests (-20°F or so) the evaporators frost up from traffic into and out of the chamber (reducing performance of the refrigeration system).  Looking for information on evaporator de-rating as ice is accumulated and sucessful stratigies to combat or reduce ice formation on evaporators.

RE: refrigeration evaporator performance

As you can see there is NO standard for this problem.  The installation simply gets more defrosts as the facility dictates.  Russell Coil in Brea Calif actually designed an infrared system to detect when a demand defrost was needed and performed one.  Thus allowing the system to perform better with no loss of product, production, and garnered energy savings.

RE: refrigeration evaporator performance

The ever-reoccuring frost-up. You find a resolution for that and you will be decorated with three bronze stars.    I took care of the sweating of toilet tanks one year by plumbing HOT water in the tank. Cold water initiated condensation, so.......
This was a two-fold accomplishment; no more wet carpet and
heat-transfer into the bathroom. A small fan gave passive
circulation as well as the evacuation fan.
SO, what system is it ? Is the evapp isolated ? What heating cycle/element does it have on it ? I need more parametric info........
                        thestocksguy@hotmail.com

RE: refrigeration evaporator performance

Buster,
Do you have more details on the design? What is your CFM? Type of refrigerant? Low temp. fluid?
What is the capacity of your de-humidifer?
You need to control the grain level (mechanical humidification and dehumidification). I did work on a wind tunnel with 50 deg. C to -40 deg. C.
If the frosting is due to the trafic (in and out) try for  conditioned air curtins.

Fayaz

RE: refrigeration evaporator performance

Hello friend. I have just signed.
The problem you have mantioned of accum. of frost on coils lowering overall performance , I had a similar problem on a chamber (Lab-line Envornmental chamber 708a-2dhx.in which I found pockets around cooling coil by-passing circulating  air . Which when tackled properly maintained temp. and humidity to the set points. Checking defrosting timer might help further.
Regards. Alley. Karachi Pakistan.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources