#3/0 Cable Resistance Test..Fail or Pass

#3/0 Cable Resistance Test..Fail or Pass

#3/0 Cable Resistance Test..Fail or Pass

(OP)
Hello All,

I recently had a a set of #3/0 Cooling Tower feeders Megged for their resistance. Two of the feeders had meg ohm results in the 1500Mohm range - 2500Meg ohm range. The readings were corrected to 40 degrees and tested at 2000V.

One of the feeders (L3 or C phase) had a resistance reading of only 729Mohm @2000V. This is almost 50% less than the resistance for the other two feeders.

Should this cable be condemmed and considered to have failed the resistance test?

Also, what IEEE standard speaks to this resistance test for a #3/0 cable and what does it say...Fail or Pass?

Attached are the readings we took.

Any help would be much appreciated in determining if we need to replace this cable based on this information and some industry standards that are foreign to me.

Thanks  

RE: #3/0 Cable Resistance Test..Fail or Pass

Need more information about the cables.

Voltage rating, insulation type.  Are there any splices, accessories included?


 

RE: #3/0 Cable Resistance Test..Fail or Pass

The low resistance is certainly suspect. Whether that's enough to warrant replacement depends on the application. If a forced outage would be very expensive or inconvenient, you might consider replacing it. If it's not so critical, you could wait a while and check it again (or not).

Alan
"The engineer's first problem in any design situation is to discover what the problem really is." Unk.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources