Can any one tell me what are the determining factors if i am about to hot tap on a longitudinal seam on a gas pipeline? what checks on the seam do i need to perform prior to cutting?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Hot Tapping
Someone needs add in here as I think OSHA has a procedure outline for hot tapping. We have our own which requires that we verify the integrity of the weld, either UT or RT and the thickness of the pipe. I would keep in mind the possible use of a slit tee which removes all stress away from the weld.
You mention no sizes or pressure/temperature. Below 4" there is equipment designed specifically for these sizes.