INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you a
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

E-mail*
Handle

Password
Verify P'word
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Member Feedback

"...Keep up the good work - excellent site - i'd been looking for something like this for ages !..."

Geography

Where in the world do Eng-Tips members come from?
stevwri (Electrical)
10 Aug 02 20:34
We are adding onto our manufacturing facility.  One electrical design uses aluminum buss duct for 480V distribution.  Another uses copper buss duct.  Aside from price, what are they advantages and disadvantges of each?
Eng-Tips Forums is Member Supported. Click Here to donate.
electricpete (Electrical)
11 Aug 02 0:14
Torqued aluminum connections can relax due to creep. That causes me concern. Even periodic retorquing may not be a good solution since it just accelerates the distortion of the components. I have seen some pretty distorted bus connection areas at our aluminum isophase bus connections where the washer causes an indentation into the adjacent bus section. I've never seen a failure yet but I don't like it.
Alex68 (Electrical)
11 Aug 02 2:44
The copper bus ducts are characterised by low resistivity and high weight, while the aluminum bus ducts are characterised by a bit higher resistivity and LOWER weight, considering the same cross section.

Usually the aluminum bus ducts are chosen when the mechanical load (weight) is a problem.
jbartos (Electrical)
11 Aug 02 3:35
Suggestions:
1. It is convenient to have all copper or all aluminum buses since the transitions from copper to aluminum and vice-versa may pose some challenges. Also, connections to transformers and switchgear could pose some challenges if of dissimilar metal.
2. For the same load, the aluminum buses will be more voluminous.
3. Since the bus amp ratings are not posted, the availability of copper and aluminum buses of your required ratings should be checked.

Start A New Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Promoting, selling, recruiting and student posting
are not allowed in the forums.
Posting Policies

LINK TO THIS FORUM!
(Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum)
TITLE: Electric Power & Transmission & Distribution Forum at Eng-Tips
URL: http://www.eng-tips.com/threadminder.cfm?pid=238
DESCRIPTION: Electric Power & Transmission & Distribution technical support forum and mutual help system for engineering professionals. Selling and recruiting forbidden.